Wind on guard rails

Status
Not open for further replies.

bookowski

Structural
Joined
Aug 29, 2010
Messages
983
Location
US
Anyone know where the 6ft referenced below comes from? I’m not questioning the logic but rather is this codified somewhere? I found a 2nd reputable article that states “between 2x to 4x” the railing height as a cutoff.

Thus, for a balcony with a depth of 6 feet or less, the wind load on the railing is similar to the load on the building windward wall (Cp = 0.8, per Figure 27.3-1 in ASCE 7-16). There is no need to consider a simultaneous leeward or suction pressure on a railing of a shallow balcony.

 
bookowski,

I got some PDH's listening to a presentation that the article author gave. I don't remember exactly what she said in the presentation, but I do have the slides from the presentation. The gist is, looking at how parapet pressures were derived, you need space behind the parapet (or solid balcony guarding) of 2 to 4 times the guarding height (as you mentioned in your post). Accepting that, a 42" tall guard * 2 will give you 84", which is about 6' with a *ahem* pocket FOS.

To the 2nd question (is it codified), well, from that same presentation:
Balcony_Wind_zywmxz.png


So no, not codified.

Please note that is a "v" (as in Violin) not a "y".
 