I am designing the foundation for an array of solar panels. There are four 15' x 18' panels attached to a continuous horizontal pipe support. Between each panel, there is a vertical column which connects the pipe support to the foundation. All four panels can rotate together about the horizontal support. Additionally, each panel can rotate perpendicular to the horizontal support - that is, the panel array can track bidirectionally.
The wind loads generated by the engineers of the superstructure use a fluid dynamics approach, and are much lower than the loads calculated by ASCE7-05 for solid signs and freestanding walls. The manufacturer of the panels states that the panels are designed for a reduced wind load, and that the panels automatically rotate into a horizontal position during a high wind event.
A couple of questions:
1. Are there any other engineers who feel comfortable designing a foundation for this retracted position? It seems to me that we should not rely on mechanical systems to reduce loads, and that the solar panels should be assumed to be in the worst case position, in which they seem to comply with the requirements for signs in ASCE7. Needless to say, difference in the foundation size for the two cases is enormous!
2. Does the IBC allow the use of fluid dynamic approaches? It seems to me that only the three methods in ASCE7 (simplified, analytical, wind tunnel) are recognized, along with the explicitly noted reference standards in the IBC (AF&PA WFCM, TIA/EIA-222, etc).
The wind loads generated by the engineers of the superstructure use a fluid dynamics approach, and are much lower than the loads calculated by ASCE7-05 for solid signs and freestanding walls. The manufacturer of the panels states that the panels are designed for a reduced wind load, and that the panels automatically rotate into a horizontal position during a high wind event.
A couple of questions:
1. Are there any other engineers who feel comfortable designing a foundation for this retracted position? It seems to me that we should not rely on mechanical systems to reduce loads, and that the solar panels should be assumed to be in the worst case position, in which they seem to comply with the requirements for signs in ASCE7. Needless to say, difference in the foundation size for the two cases is enormous!
2. Does the IBC allow the use of fluid dynamic approaches? It seems to me that only the three methods in ASCE7 (simplified, analytical, wind tunnel) are recognized, along with the explicitly noted reference standards in the IBC (AF&PA WFCM, TIA/EIA-222, etc).