Eng-Tips is the largest forum for Engineering Professionals on the Internet.

Members share and learn making Eng-Tips Forums the best source of engineering information on the Internet!

  • Congratulations dmapguru on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Wind Loads for Open Buildings of All Heights

Status
Not open for further replies.

Structural Matt

Structural
Joined
Jan 12, 2021
Messages
9
Location
US
Designing a standalone Porte cochere as an open structure and in going through Chapter 27 of ASCE7-16 I am getting stuck at determining external pressure coefficient in step 6 of Table 27.2-1. My structure has a pitched roof, so I am using Fig. 27.3-5, and this is where my problems begin.

First problem: the figure specifies that h/L shall be between 0.25 and 1.0 but my structure has a ratio of 0.20. I don't see any information on what to do if you fall outside their determined range.

Second problem: What are the two load cases given in the figure? I can't find where it specifies what the Case A and Case B are for this particular figure.
 
Second problem- bottom sentence in that figure says "All load cases shown for each roof angle shall be investigated", so I think the intent is to check with Case A then check with Case B.
First problem- I've run into this in Figure 29.4-5, where it says "0.25 <= H/D < 4.0". I'd say if you're close to the range, use the max/min in that range or extrapolate out to your point.
 
1) So how would you extrapolate? The data from the table seems to be independent of whether you are on the high or low side of the h/L range

2) It is pretty clear to check both, but I guess I'm struggling with finding what Case A and Case B are. Where are they defined? Are they the different directions the wind can come from? I.E. coming perpendicular or parallel to ridge? Like Chapter 28, figure 28.3-1 clearly shows what Case A and Case B are, but that seemingly only applies to Enclosed and Partially Enclosed Buildings
 
First question, you may refer to BS 6399-2 Wind British Standard (I added few screenshots).
Second question, the two cases are coming from enveloping wind tunnel results. ASCE 7 copy values from Australia/New Zealand wind code, British standard gives very close results. (Edit: remember those values for one direction only, for 90 and 270 degree, ASCE 7 shows different table FIGURE 27.3-7, the best to do to envelope results from both sources in each direction).
Capture_dotomb.jpg
Capture1_pldlug.jpg
Capture3_oxmjab.jpg
Capture2_uy724f.jpg
Capture4_jtlc0l.jpg
 
Status