I do not know if the IBC values match the OBC.
From the following government website I found the Cg factor.
Which gives the following statements (Though I wonder why it gives no guidance for Cp)
"Section 4.1.7. Wind Load
4.1.7.1. Specified Wind Load
(1) The specified external pressure or suction due to wind on part or all of a surface of a building shall be calculated using the following formula:
p = IwqCeCgCp
where,
p = the specified external pressure acting statically and in a direction normal to the surface, either as a pressure directed towards the surface or as a suction directed away from the surface,
Iw = importance factor for wind load, as provided in Table 4.1.7.1.
q = the reference velocity pressure as provided for in Sentence (4),
Ce = the exposure factor as provided for in Sentence (5),
Cg = the gust effect factor, as provided for in Sentence (6), and
Cp = the external pressure coefficient averaged over the area of the surface considered.
..."
and "...
(6) The gust effect factor, Cg, shall be one of the following values:
(a) for the building as a whole and main structural members, Cg = 2.0,
(b) for external pressures and suctions on small elements including cladding, Cg = 2.5,
(c) for internal pressures, Cgi = 2.0 or a value determined by detailed calculation that takes into account the sizes of the openings in the building envelope, the internal volume and the flexibility of the building envelope, or
(d) if a dynamic approach to wind action is used, Cg is a value that is appropriate for the turbulence of the wind and the size and natural frequency of the structure."
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.