dcceecy

Structural
Oct 15, 2008
112
I am calculating wind loads for an open structure roof. I use equation 6-25 p=qhxGxCn of ASCE 7-05 section 6.5.13.
The Cn net pressure coefficient shall be determined from Figs 6-18A through 6-18D. But All those figs have the requirement of 0.25<h/L<1.0. In my case, h/L is 1.33. Is it going to make a difference? Are those figs still applicable? Thanks

 
Replies continue below

Recommended for you

What does your wall pressure equal when you use those figures?
 
Yes. Look at the values in the table...they typically reduce the loading. Use the higher value or 1.0 for conservative analysis.
 
I do not have a wall. All I need is the wind load on the roof.
 