we are working on design and construction of ground grids for a wind farm.
For each 1.5 MW generator (80 total), GE is specifying ground grid resistance of 2 to 10 ohms.
With the data we have:
-ground resistivity : 500 to 1000 ohms, average
-projected ground grid area: 285 m^2, (about 3060 square feet)
First calculation (from IEEE 80-2000, formula 50 & 51):
we get ground grid resistance of 20 to 40 ohms (perfect condition), which is not bad for the type of soil we have, but still way over GE specification (2 to 10 ohms).
Two solutions came up:
1. tie all grids togheter with 3/0 AWG bare copper wire to lower the resistivity of each grid, we are confident this would work, but this solution is VERY expensive
2. Here's my question...: when the 34.5 kV power cables will be installed, if all concentric neutrals are tied at both end to each ground grid, this will have the effect of tying all grids togheter,at no extra cost, and will probably lower the resistance to satisfy GE specification.
I would like to have your opinions about this option.
Note: for grid construction, we plan to drill 3" holes in the roc, and backfill 3/4" 10' copper rods with Erico GEM. Grid conductor will be 4/0 AWG bare copper.
Thank you.
we are working on design and construction of ground grids for a wind farm.
For each 1.5 MW generator (80 total), GE is specifying ground grid resistance of 2 to 10 ohms.
With the data we have:
-ground resistivity : 500 to 1000 ohms, average
-projected ground grid area: 285 m^2, (about 3060 square feet)
First calculation (from IEEE 80-2000, formula 50 & 51):
we get ground grid resistance of 20 to 40 ohms (perfect condition), which is not bad for the type of soil we have, but still way over GE specification (2 to 10 ohms).
Two solutions came up:
1. tie all grids togheter with 3/0 AWG bare copper wire to lower the resistivity of each grid, we are confident this would work, but this solution is VERY expensive
2. Here's my question...: when the 34.5 kV power cables will be installed, if all concentric neutrals are tied at both end to each ground grid, this will have the effect of tying all grids togheter,at no extra cost, and will probably lower the resistance to satisfy GE specification.
I would like to have your opinions about this option.
Note: for grid construction, we plan to drill 3" holes in the roc, and backfill 3/4" 10' copper rods with Erico GEM. Grid conductor will be 4/0 AWG bare copper.
Thank you.