What is the affect of varying the "pitch" in the windings of a generator - is it to reduce eddy current losses and harmonic currents - we have a generator with a 7/9 pitch (so we're told).
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
The 1-9 span must be used not only to closely match the original flux densities, it is necessary because it duplicates the effective 2/3 pitch of the original winding. The 2/3 pitch (8 slots of 12 per a pole) eliminates the third harmonic in the generator output; and may be needed for paralleling to other 2/3 pitch generators.
The correct replacement for the step 12,10,8,6 (concentric) is lap 1 - 9.I recently wound a 400KW Cat generator that had a 12,10,8,6 pitch. Since I don't have basket heads that big, I wanted to convert to lap.
I converted using an 11 pitch, and ran it by EASA.
They said I needed a 1-9 pitch.
maybe I shouldn't have said dramatically higher... those harmonics are moving slow so they look approximately stationary, so the time frequency as seen by the rotor is approximately 50hz or 60hz, which is higher than the main wave frequency seen by the rotor (0 for sync machine and slip frequency for induction machine), but dramatically higher may have been misleading. This is in contrast to negative sequence fundamental where the frequency seen by the rotor can be 100hz or 120hz. I'll shut up now.electricpete said:but can impose dramatically higher time frequency for the rotor core,