eleclew
Electrical
- Jan 7, 2011
- 1
What is the affect of varying the "pitch" in the windings of a generator - is it to reduce eddy current losses and harmonic currents - we have a generator with a 7/9 pitch (so we're told).
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Correction - my post above addressed 7/9. For 5/6, both 5th and 7th harmonics are reduced (both have Kp=0..25) as zlatkodo said.electricpete said:* e [5/6] was shown in my previous post. (note 5th is reduced much more than 7th)
From the article cited above you can gather it was a competitor of Caterpillar that used 2/3 pitch. The application is relatively small generators where I gather that the need for efficient utilization of materials is tempered by a goal to produce a single machine which could adapt to multiple applications. The ability to connect the winding in delta helped this goal. In delta 2/3 pitch was useful to reduce circulating 3rd harmonics in the delta.It would be interesting to hear from CAT in which cases such a pitch is considered.
I would say what he wrote in bol is a generalization. You and I could compute more exactly how the balance shifts for a specific machine. But my basic point: certainly the savings in copper deserves to be mentioned and considered among the advantages of fractional pitch coil.I'm not disagreeing with anything you said as long as you're not disagreeing with anything I saidDesign Of Rotating Electrical Machines said:Because of short pitching, the coil end has become shorter, and the copper consumption is thus reduced. On the other hand, the flux linking the coil decreases somewhat because of short pitching, and therefore the number of coil turns at the same voltage has to be higher than for a full-pitch winding. The short pitching of the coil end is of more significance than the increased number of coil turns, and as a result the consumption of coil material decreases.
If I read the bolded portion literally, it suggest the second design = fractional-pitch coil design had higher core losses than the first design = full pitch.The first design had 168 slots and a full pitch of 12/12, the second design had 174 slots and a pitch of 10/12 3/7. The result didn't surprise me. The copper saving of the second design was a mere 105 kilograms, equivalent to a saving of US$ 1000 at todays copper prices. Nevertheless, this is a certain copper saving, as pointed out by others already. However, the loss situation was less favourable. The armature losses of the second design were 8 kW lower, as could be expected. In contrast, however, the stator core losses went up 8 kW compared with the first design.
That is why in my 17 Jan 11 10:36 post I compared 8.3% to 3.4%.... the 8.3% represented copper reduction per coil and the 3.4% represents increase in number of coils for that example.Pete: The copper reduction per coil for the second hydro generator design is (1 - 5/6) * 0.42, but you have to add the copper weight of 6 coils.
That part was a point that I did not correctly describe, good point. Looking among a variety of machines I think faster machines tend to have higher ratio "X" than slower. But does not apply for large turbo machines.I guess that for large 60 Hz 2-pole machines the X-figure will be in the region of 0.25 or even below.
Please explain to me the logic of your 17 Jan 11 12:59 statement: "I'm not disagreeing with anything you said as long as you're not disagreeing with anything I said".