In the attachment, it says "Control power to the Shunt Trip with Lockout must be removed for a minimum of 0.25 seconds before the breaker can be closed". Why wait for 0.25 seconds what is logic behind it.
Can only assume that it's a conservative thing to ensure that the shunt trip actuator is fully retracted (disengaged?) prior to attempting to close the breaker. The alternative is that the breaker keeps tripping on close as the shunt trip is still engaged.