I don't think I could explain it better than imok2. One thing to be aware of many two stage cooling units have two compressors. But if the enthalpy of the osa is lower than the return air enthalpy, the enthalpy controller switches the first stage cooling to osa/mixed air control, and second stage cooling becomes the number one compressor. Many times the first stage condenser fan is cycled off a pressure switch and the second condenser fan is enabled on an ambient temperature switch. This is a rather antiquated an inexpensive set up, today many manufacters are using VSD on their condenser fans. Just my two cents