Why is LL bigger than 3ph fault
wonderchi
36
I have just obtained some fault currents result from using SKM, it shows that both the SLG and LL(phase to phase) is much higher than the 3ph fault.
With SLG fault I can figure out that it is possible (due to low sequence impedance) but why is the phase to phase fault bigger than the 3ph fault?
Correction...
it should be LLG (double phase to ground fault) not LL....
Why is LLG bigger than 3ph fault? Because of low zero sequence impedance from generators and transformers?
Delta/wye transformers ahead of the fault location short circuit the upstream zero impedance network regardless of fault type. Any fault involving the zero sequence network will see a low zero sequence value.