stookeyfpe
Thanks for the offer. I believe I have a plan worked out but I would really like to see your comments.
We are currently building two buildings. The first is a 15,000 sq ft mixed use building. Office space, boiler room, compressor room. Building shell is a prefabricated metal building with metal studs and drywall internals. Should fall under IBC Type IIB. Sprinkler Design is 0.3gpm/ft2 over 5000sqft.
The second building is a batch chemical production building utilizing Class 1A flammables. It is 10,000 sqft with a 3000 sqft mezzanine. It is a tilt up concrete building, so under the IBC it is also a Type IIB. Sprinkler design is 0.3gpm/ft2 over 5000sqft.
We are also building a tank farm that has a foam suppression system with a coverage requirement of 0.16 gpm/ft2 over a total of 11,400sqft, and two fire monitors that require 750gpm each. (Covers seven 30,000 gallon tanks, two 8000 gallon tanks, and a railroad tanker unloading bay.)
The rest of the campus is set out in the future. It will consist of more of the production buildings and some warehousing of chemicals.
Fire hydrant demand is set a 750gpm.
In the 2006 IFC appendix B it sets the flow at 2500 gpm for a 15000sqft Type IIB building, before you take credit for the sprinklers.
However if you look at our current largest demand you get 1824 gpm for the tank farm and 1500 gpm for the two fire monitors that go with the tank farm suppression system. That gives me a flow of 3324 gpm with no fire hydrants running. If I add one fire hydrant (750gpm) to the mix that puts me at 4074 gpm.
So I don't think that it is unreasonable to set the fire flow demand at 4100gpm.
However that means anything else I build has to fall within this envelope.
What do you think?
Thanks
StoneCold.