Hi there,

I am trying to determine the actual Kw cost of a motor being run via a VFD.

Where is the best place to measure the values I and V as there is differnces on the incoming supply to the load side of the VFD?

Thanks in advance.
Thomas

 
Replies continue below

Recommended for you

Since actual kWh cost, not kW cost, is measured on the line side, that is where to put your kWh meter.

Measuring V and I won't help much. Nor will measuring kW. Unless it is very constant over time. Cost is energy based and that is kWh.

Gunnar Englund
--------------------------------------