NFPA 20 Handbook, "It is important to note that the scope of NFPA 20 stops at the discharge control valve, and nothing in NFPA 20 prohibits the use of pressure-regulating devices downstream of the discharge isolation valve."
With that said, you will have to look at other standards downstream the control valve that govern the system to see what are the requirements about PRVs.