“Based on mike's comment that ethylene rather than ethylene is the dominant gas, I now believe that an actual hotspot is a more likely explanation than my previous proposed explanation arcing type LTC. “
rraghunath - you had some comments about leaking between tank and LTC compartment. I assume all gas measurements here are in LTC compartment. But maybe deserves some clarification from Mike. Also is the Buchholz on the LTC or main tank?
Mike - fwiw I agree with Steve that lack of cycling is a known cause of coking. Many utilities whose LTC’s do not cycle over the full range require periodic manual cycling which includes forcing the LTC to excercize the reversing switch.
I had some direct experience with gassing of a Westinghouse type UVT LTC on two occasions 10+ years ago. I don’t remember the gases but I’m pretty sure ethylene was hightest. Levels I think got around 2,000ppm at highest. I also remember 8C rise from bottom to top of LTC tank by infrared. Found massive damage on one of the selector switch contacts. The first time we attributed it to infrequent cycling. We instituted periodic manual cycling requirements. Very similar symptoms recurred a few years later and again found severley degraded selector swtich contacts. We identified two additional possible causes: 1 – high moisture in LTC oil up to 75ppm; 2 – contact material. We upgraded our dessicant breather to a better style and installed silver-plated contacts from high-voltage engineering. Problem has not recurred since then.
=====================================