Without VFDs it is no issue at all. You will get your energy savings simply by the lower flowrate through the plant alone. Whether you will get more energy savings, if you use VFDs, is entirely another question. Over the last few years, I have studied the application of VFDs to new plant and facility designs and have found out that generally speaking,
With VFDs, pump energy essentially increases to 5% more than what you would use with simple constant flow at the optimum BEP speed design flow.
At around 50% flow, your energy consumption is obviously roughly 1/2, based on 1/2 Q alone, Power = q[ρ]h/e, neglecting some efficiency decrease. You have a potential to save money, if you can also cut H, but with VFDs you must be able to cut H by the drop in speed squared to move any flow. So, that's 1/4 H at design speed, a drop to 0.5 squared. Lots of plants can't do that.
So, generally speaking again, you can't drop to 50% with VFDs in many applications. If you do, you don't save all that much over constant speed operation, because you've already saved half anyway simply by cutting plant output in half, so there's only a max you will save around 25% at best, not half.
Here's the killer. Yes, if you operated the plant at half flow you might could save money with VFDs, but do you want to operate at half flow? NO! You've already cut your profit in half. There is no business reason to do it, so if you do, you will only run at half flow for the smallest amount of time possible, or your boss will kill you. Now let's push up toward higher flowrates again.
As you get to 75% to 85% operation, there is some potential to save money with VFDs, you're in the good range for that, but if you move to operation at 80 to 90% design for enough time where it makes it attractive to use VFDs, I've found that you should really review your design flow criteria and most likely lower that to the point where you can go back to running the plant continuously at a full speed operation again, just at 90% of the design flowrate that you thought you needed before. When applying VFDs to new plant design, if it looks attractive, it could easily turn out that you probably made a bad choice of original design flowrate and you should reduce that by 10 percent or so and run at constant speed. If you selected your design flowrate conservatively to have some easy future expansion capacity, then, if you were so optimistic then, you shouldn't now be looking at running at 75% or less design flowrates where VFDs make sense. VFDs have some potential to save in closed loop systems, where you may never want to operate at maximum flow for a very long time, otherwise ... well .... look elsewhere for energy savings. There ain't any there.