DanDel,
In the case of an ungrounded system, with one phase to ground fault, the voltage of the faulted phase will be pulled all the way down to ground and the other two phases will have a phase to ground voltage equal to their phase to phase voltages. Voltage shift does not require current flow. In the example just cited, the three sequence voltages will all be 1/3 the prefault voltage magnitude where as the prefault sequence voltages will have been 1 per unit positive sequence and zero per unit for the other two.
If you can accurately determine the correct impedance to plug into your formula without the use of symmetrical components analysis, you are far better at circuit analysis than many of the great authors of the field (of whom I dare not compare myself). I have yet to see a circuit analysis text tackle a single line to ground fault without symmetrical components. A fully developed analysis that does not use symmetrical components but arrives at the same fault current value as a symmetrical component analysis would be most welcome and could be your claim to fame.
In the problem at hand, even modified sufficiently that a meaningful result can be achieved, what value do you propose for your R-jXC? Do you use prefault or post fault XC values (voltage changes, therefore capacitive reactance changes)? Where did the +jXL disappear to? If it were a single phase system it would make the calculations much easier, but circuit analysis of three phase systems under unbalanced conditions does not lend itself to such simplifications.
Now, I've said what I have to say, I'll let you have the last word, and that, hopefully, will be the end of this, since it doesn't look like either of us will convince the other.