We are having an internal debate - what R value is appropriate for a 1-story pinned-base moment frame with several bays? (no seismic detailing - see attached image).

Side 1: Moment frame provisions apply, R = 3.

Side 2: Column is in single curvature and moment frame provisions do not apply. Behavior is more like a cantilevered column system w/ R = 1.25 or an inverted pendulum type structure w/ R = 2.

Thanks for all your input!
 
 https://files.engineering.com/getfile.aspx?folder=3363978c-1f1c-4f3d-90b0-82a1e4666d67&file=Brace_Question.jpg
Replies continue below

Recommended for you

If you're not providing any seismic detailing (not detailing per AISC 341), then you'd fall into Steel Systems not Specifically Detailed to Resist Seismic Loading - R=3.
 
I'd go with R = 3. The major difference from an inverted pendulum or cantilevered column system is that rotation will be fixed at the top for the pinned base moment frame.
 
R = 3. There's a lot more redundancy than you'd get with an inverted pendulum or cantilevered column.
 