In the last years, our substations have been hit by significant earthquakes (e.g. in Aquila in 2006, PGA=0.675g and Emilia Romagna, PGA>0.3 g).
Some equipment suffered heavy damage and had to be replaced: 420 kV CBs were find to be the weakest point.
Our EHV/HV ATRs, which were not fixed to the ground, did not suffered heavy damages: only in one case 420 kV porcellain bushings, which were actually rated only up to 0.3 g, were damaged.
In fact active part of the transformer is designed to resist significantly higer mechanical stress durind transportation (often exceeding 0.5g) and during short circuits. Use of RIP bushing with silicon housing, will substantially reinforce the transformers, which however even without anchoring are probably the most robust equipment in a substation, if compared to CBs, CTs and VTs...