I have been using thermal cameras for building envelope work for over 30 years. They can be great tools, but can be misleading as well, particularly when used by those who don't know their limitations.
As others have noted, they don't find moisture. They find, perhaps, indications of moisture based on a thermal signature. They are, at first, visible thermal anomalies that have to be verified by a secondary means, preferably by destructive observation and sampling. A secondary means can also be another nondestructive approach (capacitance meters, nuclear moisture gage, etc.); however, to get irrefutable evidence, cutting into the material and observing and sampling materials for laboratory determination of moisture is preferred.
In a building it is easy to get a lot of false anomalies. As an example, you use a thermal camera to observe an exterior wall and you see a thermal indication. Is it moisture or is it some appliance or device on the interior that is causing the wall to heat up? Each of the anomalies can be a rabbit hole that has to be run down.
As for cameras, there are lots of them on the market....some good, some not so much. I have a FLIR camera that costs about $20,000. It is pretty good and I get it calibrated periodically, which costs about $500 to $1000 each time. Not a cheap process but if I am putting my reputation out there based on its use, I want it (and me!) to be right!