To take that a step further, never specify "Fail Safe" for a valve (or anything else). You need to select a failure direction that is safe. For example, a fail-closed valve on the discharge of a positive displacement pump would be anything but safe since a couple of strokes after the valve fails, a PSV is going to go off or something is going to break.
Sometimes it is a bit grey whether a valve should fail open, closed, or as-is. That is where Engineering Judgement comes into play. You (as the system designer) have to look at every actuated valve and decide: (1) what does failure mean; and (2) in a failure what direction should this fail. For example, many pneumatic valves have solenoid valves sending pressure to them. You need to think about what should happen on both a loss of air pressure (both global and between the actuator and the solenoid) and a loss of electrical pressure. This can be tough but is necessary. For this example, if you have a thread leak between the pneumatic actuator and the solenoid valve, what do you want to happen? Most of the time I would say that I want the valve to be in its depressurized state between activations (i.e., a dump valve should be pressure to open, vent to shut) so a leak like this is no big deal. Sometimes that is not possible and you need to think about it.
Hope this helps. Important thing is to realize that "Fail Safe" is a mass media term that will get a system designer into all sorts of trouble.
David