What is meant by REF cable for a transformer

Status
Not open for further replies.

masalah

Electrical
May 10, 2010
27
Dear all,

What is meant by REF cable for a transformer exactly in details please.

Thank you.
 
Replies continue below

Recommended for you

It is difficult to say definitively without the full context, but my guess would be Restricted Earth Fault cable. Restricted earth fault protection is applied to the star winding of a transformer. It protects the zone bounded by the REF current transformers. The REF cable would probably be the cable from the REF current transformer in the transformer neutral to wherever the REF protection relay is located.

Regards
Marmite
 
Thank you Marmite again :)

Yes it is appearing in the typical protection layout of the LV switchgear ...

So I think that your understanding is ok. RESTRICTED EARTH FAULT ...
 