Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

what is density of bitum.concrete 1

Status
Not open for further replies.

johny13

Structural
Joined
Sep 8, 2011
Messages
15
Location
US
i am taking 25psf/(2"/12")=144pcf..is that okay?
 
I am sure there are numerous other resources for this and many DOTs have a rating manual or guide that will list various material data specific to their own agencies.

That said, AASHTO list this value closer t 140 pcf.

Regards,
Qshake
[pipe]
Eng-Tips Forums:Real Solutions for Real Problems Really Quick.
 
it depends on the aggregate used and degree of compaction. call your local supplier or paving contractor if you want an accurate number. By the way, you need to re-check your math...
 
I have often seen 25 psf used for a 2 inch thick asphalt overlay. 25 psf / 2" x 12" = 150 pcf.

AASHTO says to use 150 pcf dead load for pavement other than wood block and 140 pcf for macadam or gravel, rolled.

 
1) When calculating in inches asphalt weighs 12 lbs/sqft, exactly. That way you can just multiply by 12 and not touch the calculator.

2) When estimating quantities asphalt weighs 150 pcf, exactly. Because you don't want to come up short, even by 4%.

False precision breeds the lie that engineering is "exact".

I agree with what the others wrote, but couldn't help adding my two-bits.
 
Typical dense graded structural mixes will range between 135 and 145 pcf.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top