What is better for a ground system - THW or THWN?

Status
Not open for further replies.

downtownfool

Mechanical
Joined
Dec 6, 2012
Messages
6
Location
NL
All i find on the two is this:



THW (5) 75¡C 167¡F 90¡C 194¡F
DRY & WET LOCATIONS SPECIAL APPL. WITHIN ELECTRIC DISCHARGE LIGHTING EQUIPMENT LIMITED TO 1000 OPEN-CIRCUIT VOLTS OR LESS, (SIZE 14-8 ONLY AS PERMITTED IN SECTION 410-31).
MOISTURE AND HEAT-RESISTANT THERMOPLASTIC



THWN (5) 75¡C 167¡F DRY AND WET LOCATIONS


Is there a real benefit of one over the other with regard to buried ground system?
 
Personally, I'd use bare for a buried ground system.
 
I'm told they can't due to catholic protection and other reasons.
 
The whole point is ground contact. Insulated conductors aren't so hot in that arena.
 
When faced with a choice such as this, I generally use the cable type that is in stock locally. That is unless there will be a lot of buried electric discharge lighting equipment. And I echo davidbeach's comments.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Look up ufer ground if you're trying to avoid soil contact.

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
The THW insulation will be thicker than the THWN and more resistant to physical damage, but not sure if there is any real difference in the resistance to ground in a buried installation over time.
 