Hello,
Some info is in order first I suppose. I have a substation, fed via a 34.5kV (3 wire) line. Transformer is 34.5/7.2kV Delta/Gnd-Wye. The fault current is 2kA on the 34.5kV side. Rg=2.8ohms This sub is also tied to the 34.5kV source sub via two 7.2kV (4 wire) distribution lines.
Now I get lost at determining which IEEE80 Appendix C split current curve to use here. I don't see much in any searches on this subject. Would I use the curves for 100% remote source and 0 transmission lines and 2 feeders?
Thank you,