In Georgia they are about to change the rules. It is a final draft and this is going to happen.
Found on the updated draft of:
On page 11:
It appears the layout technician is to follow the specifications while alerting the state fire marshal to specifications that may be non-compliant.
For example both the Georgia Fire Marshal and the Georgia EPA (Water Quality Board) requires a minimum suction pressure of 20 psi, at the pump suction flange and throughout the public water system, when fire pumps are operating at 150%.
I am looking at a job where there will be a negative suction pressure of minus 15 psi with the pump operating at 150%. What do I do, bid it to get it seeing a change order in my future? Who pays the $300k for the water storage tank?
What about the classic mercantile where a design density of .15/1,500 was specified? Yeah, ran into this three weeks ago and I bid it to a .20/1,500.
If I am reading this correctly it is the design professional of record who gets to explain all this to his licensing board. Imagine trying to explain why the mistaken design criteria specified should be the problem of the layout technician? I can't see how arguing with his licensing board would be a good experience especially if it's the layout technician who was charged with alerting to the problem.
Reading the entire document makes clear the Georgia Fire Marshal is out to make sure things are done the right way. For those that don't know, or don't care, sloppy work can put one in line for some real brutal treatment.
Found on the updated draft of:
The Rules and Regulations of the Safety Fire Commissioner are hereby amended by repealing Chapter 120-3-19 entitled, "Fire Protection Sprinkler Contractors" in its entirety and substituting in lieu thereof a new Chapter 120-3-19 entitled, "Rules and Regulations for Enforcement of the Georgia Fire Sprinkler Act," to read as follows:
CHAPTER 120-3-19
RULES AND REGULATIONS FOR ENFORCEMENT OF THE "GEORGIA FIRE SPRINKLER ACT"
On page 11:
(3) Non-code compliance dictated by bid documents shall be reported in the following manner: Non-code compliant shop drawings dictated by bid documents plans and or specifications shall list deficiencies printed or typed, item by item, along with codes and/or standards violated on a departmental form. In addition, the following information shall be provided as set forth in the following order:
(a) The name of the facility and project;
(b) The complete physical address of the project including the city and county;
(c) The owner's name;
(d) The responsible architect's or engineer's name responsible for producing the non-code compliant bid documents including their Georgia registration number, business name, business address and business telephone number; and,
(e)The Sprinkler Contractor's name, Certificate of Competency holder's name, and Certificate of Competency number and signature. The foregoing items shall be provided and outlined on a departmental form by the Certificate of Competency holder, as stated above and shall be submitted with the shop drawings.
It appears the layout technician is to follow the specifications while alerting the state fire marshal to specifications that may be non-compliant.
For example both the Georgia Fire Marshal and the Georgia EPA (Water Quality Board) requires a minimum suction pressure of 20 psi, at the pump suction flange and throughout the public water system, when fire pumps are operating at 150%.
I am looking at a job where there will be a negative suction pressure of minus 15 psi with the pump operating at 150%. What do I do, bid it to get it seeing a change order in my future? Who pays the $300k for the water storage tank?
What about the classic mercantile where a design density of .15/1,500 was specified? Yeah, ran into this three weeks ago and I bid it to a .20/1,500.
If I am reading this correctly it is the design professional of record who gets to explain all this to his licensing board. Imagine trying to explain why the mistaken design criteria specified should be the problem of the layout technician? I can't see how arguing with his licensing board would be a good experience especially if it's the layout technician who was charged with alerting to the problem.
Reading the entire document makes clear the Georgia Fire Marshal is out to make sure things are done the right way. For those that don't know, or don't care, sloppy work can put one in line for some real brutal treatment.