What cable glands do I used with “Ex emb IIC T4” rated LED lights in hazardous area?
I think we should use ex ‘e’ glands, but my colleague who’s 30 years older insisted on using non-atex glands. Because “it’s cheaper and we are not using ex‘d’ equipment, so we don’t need integrity of the system, we just need the correct IP rating”. I agree with him on the IP part. I’m very concerned with the safety of the system if a fault does occur.
I checked the standard IEC60079-14 Edition 4.0. Under the “Additional requirements for type of protection ‘e’ – Increased safety” section, I only managed to find the requirement of maintaining the IP ratings. Nothing about using ex ‘e’ glands for ex ‘e’ enclosures.
Although in the standard IEC 60079-0, it stated “Cable glands, when installed in accordance with the instructions required by Clause 30, shall not invalidate the specific characteristics of the type of protection of the electrical equipment on which they are mounted.” – does this requirement apply to Ex ‘e’ equipment or just Ex‘d’ equipment?
What’s the real benefit of using Ex ‘gland’? Is my colleague correct all along and I’m the one who’s being too fussy for no reason?
Thank you,
I think we should use ex ‘e’ glands, but my colleague who’s 30 years older insisted on using non-atex glands. Because “it’s cheaper and we are not using ex‘d’ equipment, so we don’t need integrity of the system, we just need the correct IP rating”. I agree with him on the IP part. I’m very concerned with the safety of the system if a fault does occur.
I checked the standard IEC60079-14 Edition 4.0. Under the “Additional requirements for type of protection ‘e’ – Increased safety” section, I only managed to find the requirement of maintaining the IP ratings. Nothing about using ex ‘e’ glands for ex ‘e’ enclosures.
Although in the standard IEC 60079-0, it stated “Cable glands, when installed in accordance with the instructions required by Clause 30, shall not invalidate the specific characteristics of the type of protection of the electrical equipment on which they are mounted.” – does this requirement apply to Ex ‘e’ equipment or just Ex‘d’ equipment?
What’s the real benefit of using Ex ‘gland’? Is my colleague correct all along and I’m the one who’s being too fussy for no reason?
Thank you,