If you have already spent the money on a VAV zoning system and you have a need for heat on the exterior zones the cost to install parallel fan powered boxes is an incremental cost. You've already paid for the VAV air handler, the controls, the VAV box, and the reheat.
You now have the added benefit of not needing as much reheat since, as lilliput1 said, you are reheating the relatively warmer plenum air. Which means smaller heating coil requirements. (75 F to 90 F vs 55 F to 90 F) There is a payback both in first cost (smaller coils, smaller gauge wire or smaller hot water pipe and boiler), and energy usage when heating during occupied times.
When you look at unoccupied times you don't have to run a 20, 30, or possibly 50 HP fan motor to heat one exterior zone that needs heat and can just run the VAV box's 1/4 HP motor and recirculate the air in that one zone.
Those are the reasons I would "waste" the money on the boxes .