Wet Pipe Slope per FM

Status
Not open for further replies.

bmlxd40

Mechanical
Joined
Oct 7, 2011
Messages
82
Location
US
At one time,I believe there was an FM requirement for wet pipe to slope for drainage. I don't see the requirement in the most current version of Data Sheet 2-0. The the requirement go away?
 
I believe edition 2010 is the one you are looking for. See 2.5.2.4 which did not apply to any specific system, rather all. Since 2014 the clause was change to read "Pitch of Dry-Type Sprinkler System Piping".
 