One of our heaters has a transformer that had load connected between primary and secondary windings. Can anyone give any thoughts on what does this type of connection mean... any ideas would help...

Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Each string of heaters will have 1/2 of the L-N voltage across it. I don't see the advantage of this over just having two strings in parallel, with string each rated for full L-N voltage. No matter what happens to one string (except having a complete short), it won't affect the voltage across the other string. The autotransformer arrangement does nothing to stabilize the current. It will be (VL-N/2)÷R.The autotransformer will split the supply voltage, and will thus stabilize the neutral point between the series loads. Should one of the heater strings open up, current will bypass the open string, but maintain the proper voltage on the remaining string.