I have a W16x57, with a 7'-6" cantilever, supporting common roof trusses at 24" o.c.
In such a case, I always provide (1) set of web stiffeners, same or greater thickness as beam web, each side of web, directly above the cantilever supporting column.
Although I've never done so in the past (I frequently design "long" cantilevers), I'm considering providing web stiffeners 12" to 24" o.c. from supporting column, both sides of column for one or more space(s). But... I don't want unnecessary labor = $$$.
In this particular case, my shear is only 21% stressed.
What are your standard practices?
I often see details of either (2) sets of stiffeners - (1) each side of column; or (3) sets - (1) each side and (1) directly above column.
Although it HAS not happened in the past, i consider that that long of an unbraced cantilever may tend to torque or buckle.
Any thoughts? Am i overthinking?
Thank you!