Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Watts to BTU calculation 1

Status
Not open for further replies.

malz

Mechanical
Joined
Mar 29, 2001
Messages
11
Location
US
Looking for the calculation which converts watts per sqare foot, to BTU then to refrigeration tonnage. Any help would appreciated.
 
1 watt per square foot is approximately 3.14 btu per square foot
 
Thanks!!
 
please note that conversation factor is 3.44 (not 3.14)
 
Isn't 3.413 Unless my Teachers are wrong... Which is entirely possible.
 
Gentlemen you are forgetting the basics here !!!

You can not convert watts/ft2 to BTU because you can't compare power/area with energy Steven van Els
SAvanEls@cq-link.sr
 
In the UK we have gone through this conversion thing already, so here is typical conversions used

Power

kW -> BTU/hr(x 3412)
Tons Refrigeration -> kW (x 3.517)

Intensity of heat flow rate

BTU/hr square foot -> W/square metre (x 3.155)

Typically for budget cooling load estimating we use 140 W/square metre.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top