YUSNIDA83,
As you my know, water treeing in power cable is a topic that has been discussed since the 1970's. Currently there is no commercially available way to pinpoint water treeing in a cable system.
We have a great deal of experience performing Tangent Delta (TD) tests in the field with our clients. While it is true that a correctly applied TD test can detect losses caused by water treeing and can be a useful tool, it also measures losses coming from all other cable system components. TD cannot locate losses but, it simply provides a value for the entire cable system under test. Most TD sets for field use do not use a guard circuit to bypass leakages on the surface of terminations. Losses coming from joints and terminations are sometimes 10, 100, or 1000 times larger than that which the cable component manufacturers recommend. Yet, "leakage" on the surface of a termination is not typically an issue of concern. Also there is no commercially available method to calibrate the TD test in the field to assure that the results are accurate. I know of a case study where someone replaced approximately 36 out of 48 terminations (78%), and found that the TD of the cable system improved by more than a factor of 10. When asked, how they knew which termination to replace, they stated that the always replace both because they couldn't tell. This of course was good news for the testing company because they were also the repair contractor. In the vast majority of field test studies that I have reviewed, TD values on aged solid dielectric cable systems are much higher than manufacturers' recommendations for new systems and (on a standard basis) would be recommended for replacement. Thus, a TD test on aged cable is many times a self fulfilling prophesy. Some of our clients have called it the “calendar” test as aged cables typically have higher losses than newer cables.
On the other hand, we have found that an offline 50/60Hz PD test, is very effective at finding electrical trees which are associated with water trees. After all, the only water trees that are likely to go to failure are those which initiate an electrical tree (small tree like fault channel). Since electrical trees typically only grow during voltage transient situations and are delayed in growth due to the water tree, they typically take years to go to failure and are observable and can be pinpointed by a standardized offline 50/60Hz PD test which is calibrated in the field and demonstrates better than 5pC sensitivity (cable component manufacturers’ requirement). While this approach can not detect losses, unless they are associated with PD, most of our clients prefer the PD test as it is much more precise, it is comparable with standardized factory PD tests and the results and can be calibrated and verified in the field.
I would like to caution you to use consensus documents as a reference. (IEEE, IEC) Many of the available documents are not consensus documents and are written by the organization performing much of the testing (a biased position). In addition, we typically only recommend studies in which there are control and experimental data so that actually performance of tests and cable systems can be compared.
Happy New Year!
Cheers!
Benjamin Lanz
Past Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants