"They won't if the tank pressure is high relative to the disch head of the pump, besides which a tank should be sized to provide flow at high demand anyway, thereby making the purpose of a vfd pretty much redundant, even if it could be made to work properly." BigInch
My thoughts on a tank are that the VFD is holding a steady 130 PSI, so how can the tank deliver any water? I have found that even with a tank on line, a VFD pump has to start when even the slightest amount of water has been used.
"Regarding static head on start-up. If your well is deep, the well water will drain back down the well on pump shutoff. Deep well pumps have internal check valves that allow the water to drain back down. So the static pressure will not be large on start-up. You are not starting against system pressure." bimr
Starting against system pressure or a closed valve is the best way to start a pump. Starting with no head against the pump will cause upthrust on the pump and overload the motor, which is not a good thing.
"The VFD is beneficial if the water level in the well will vary. With a fixed speed pump, the discharge pressure will change as the water level in the well varies." bimr
With only a 50' setting, the water level won't vary enough to make any difference.
"You probably should buy a VFD with bypass. The bypass feature allows you to run the VFD at 100% capacity and will mimic the operation of a fixed speed pump. " bimr
I would also recommend a bypass. Especially in such a remote location. You will still need a pressure tank to run the pump on bypass. Just doesn't sound like a good application for a VFD. Of course I have just been bitten by a similar application of a VFD, so I am gun shy.