Water Sample Analysis 1

Status
Not open for further replies.

Inchtain

Petroleum
Joined
Feb 21, 2021
Messages
151
Location
LY
Hello,

A water sample from the drain of a Crude Oil storage Tank was analysed with the below-mentioned results.

To what extent do you think it is being corrosive?

PH: 8.6
Conductivity: 4395 US/cm
Salinity: 2747 mg NaCl/L
TDS: 2666 mg/l
Chlorides: 1665 mg/l
Sodium: 1081 mg/l
T. hardness: 95 FD
Calcium: 260 mg/l
Magnesium: 72 mg/l
Carbonate: Traces
Bicarbonate: 1281
Sulphate: 0.09 mg/l
Nitrate: 8.0 mg/l
Iron: 1.23 mg/l
SRB: Nil

Thanks[tt][/tt]
 
Have you bothered to calculate an LSI (or whatever index you use)?

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed
 
The water is supersaturated with respect to calcium carbonate and one would expect some scaling.

The water will be corrosive because of the high levels of sodium and chloride. The iron level indicates a corrosion product.