gtsim,
Why bother with wet compression? Good question. Since wet compression works basically by evaporating water in the compressor as long as the inlet temperature is above 45F your gain in power is constant. For Frame machines a good rule of thumb is that for every 1 GPM of water put into the compressor you will get 160 kW of additional power, In simple cycle frame applications for each 1% of mass introduced the heat rate is reduce by about 1.25%, and the NOx is reduced on conventional combustor machine about 25%. As an example take an 80 mW (ISO) class machine operating in simple cycle with a 95F dry-bulb 73F wet-bulb design point with no cooling its output would be approximately 70mW. Put fogging on the machine, say 21 GPM, you will have about 5mW more power with a 2.5% reduction in heat rate, add wet compression say a 1% system you would add another 42 GPM of water and gain an additional 6.7 mW of with a reduction in heat rate of another 1.25%, so you total power gain would be 11.75mW for a total 0f 81.75 mW with a reduction in heat rate of 3.75% at the design point. Take that same machine and chill it to 50F using electrical chillers. As a net gain one would expect no more than 15% improvement in output with little to no impact on heat rate. So your output would be 80.5 mW. The chiller system would require about 200 GPM of make-up water for the cooling tower, plus maintenance of the rotating equipment. One could install chilling and wet compression together and get 80.5 mW + 6.7 mW to get a total of 87.2 mW gain. Also consider the plant will not always operate at design point, thus the net gain in output will vary with fogging, evaporative media, and chilling, so one would need to look at the net gain over the expected plant operating time. Now in most cases the fogger and CWCT will cost about ¼ to 1/3 of the chiller system, so one might consider it on mature robust machines, by weighing all the risks versus the rewards. Just a side note the LM6000 has wet compression as a standard offering as E-Sprint.
The nice thing about absorption chillers are the very lower parasitic losses, they do tend to have higher maintenance cost, and do not like to operate at part load conditions, so a combination of absorption and compression maybe an attractive method.
The 1990 project was actually designed it to cool the inlet air to 42F. The owner had been warned of the potential for icing and decided to experiment with temperatures, In theory icing occurs due to the acceleration of the air as it is going into the compressor. In the different papers presented on this topic, the temperature depression is between 8 and 10F. In this case icing did not occur, but you are correct there was the possibility.
Hope this helps you, but may have only raised more questions which is good also!