You need to use the static pressure (no flow), then draw off all of the demands (including upstream), and make sure that you have at least the required residual pressure at the highest point along the line after you have taken off your subdivision load. You will also probably need to check with a fire flow in addition to normal loads.
If you cannot meet the required residual pressure you may have to increase the pipe size.