water heater sizing

Status
Not open for further replies.

engineeringveda

Civil/Environmental
Joined
Dec 5, 2007
Messages
1
Location
US
When sizing a water heater for the central plant of a multi unit condo, statistically how many showers are being used at one time. 100% of the users, 50% ?
 
As per ASHRAE Systems handbook, use 0.3 as a demand factor (for apartments), 1.25 as storage factor. Probable demand = Total demand (GPH) x 0.3. Storage gallon = Total demand (GPH) x 1.25=gallons.

The ASHRAE factors are of course, an average. You should consider also, how the condo owners live. Do they all get up at the same time for showers? Do half? Do some shower at night instead of morning? Talk to the owner or architect. If in doubt, use .75 for demand factor. They won't get mad if they don't run out of hot water.
 
Consider that the cost of the heater is divided amongst all the owners, both sunk and variable, so a slight oversize is probably not noticeable.

TTFN

FAQ731-376
 