bdk
Mechanical
- Feb 2, 2007
- 6
I am currently reviewing some shop drawings from a local contractor. In there calculations they have not included the fixed pressure loss for water flow switches. The project is being designed to NFPA 13, 1999 edition. I believe that a flow switch is considered a “device that affects sprinkler discharge”. After reading the Memo from Potter dated 11/24/03, that explains the friction loss for a flow switch is 3 psig for sizes 4 in. or less and 1 psig for sizes exceeding 4 in.
Under the '99 code, section 8-4.4.5 Pipe friction loss shall be calculated in accordance with the Hazen-Williams formula with C values from Table 8-4.4.5.
(a) Include pipe, fittings, and devices such as valves, meters, and strainers, and calculate elevation changes that affect the sprinkler discharge.
In the ’02 code, section 14.4.4.5, the above was changed to “(1) Include pipe, fittings, and devices such as valves, meters, flow switches in pipe 2 in. or less in size, and strainers, and calculate elevation changes that affect the sprinkler discharge.”
I am wondering what the over all consciences is of requiring them in calculations?
Under the '99 code, section 8-4.4.5 Pipe friction loss shall be calculated in accordance with the Hazen-Williams formula with C values from Table 8-4.4.5.
(a) Include pipe, fittings, and devices such as valves, meters, and strainers, and calculate elevation changes that affect the sprinkler discharge.
In the ’02 code, section 14.4.4.5, the above was changed to “(1) Include pipe, fittings, and devices such as valves, meters, flow switches in pipe 2 in. or less in size, and strainers, and calculate elevation changes that affect the sprinkler discharge.”
I am wondering what the over all consciences is of requiring them in calculations?