3-phase Y/Y connected VTs have 3-phase, 4-wire secondary distribution. Now, there is option to earth the 4th or star point of the VT secondaries or to earth one of the phases.
While it is standard practice to earth the star point, in some cases, specifically in case of unit connected generators, it is preferred to earth the Y-phase rather than the Star point.
The advantage with this is that the earth fault protection in the generator system can be set without any fear of it maloperating for a phase-to-ground fault in VT secondary circuits.
IEEE C57.13.3 Grounding of Instrument Transformer Secondary Circuits is a good reference.