Industrial location. 3 phase 480V delta source - 25A Fused Disc (in a remote location, capable of being locked out) feeds a 15KVA delta-whye drive isolation xfmr (18FLA) (#10 wire). The secondary of this xfmr immediately feeds a 10hp VSD (within 10 feet), which in turn supplies the 10hp motor (#10 wire) (in another remote location).
The questions I have are this:
1. Does a disconnect need to be within sight of the VSD?
2. Because the xfmr is fused on the primary @ 125%, it does not require secondary protection. Does the VSD, which provides electronic OL protection, meet the requirements for transformer secondary CONDUCTOR protection requirements?
Thanks