It should also be pointed out that vortex generation depends on the flow and outlet pipe size. If you have low velocities, a vortex will not occur.
Inadequate submergence can result in rotation of the water in the tank, resulting in the formation of strong free-surface air core vortices and the entrance of air into the pump suction inlet. This phenomenon is commonly called vortexing.
Vortexing can cause unstable pump operation, vibration, pulsation and severe mechanical damage.
The U.S. based Hydraulic Institute has produced the following guidelines for recommended minimum submergence of the pump suction inlet to reduce the probability that strong free-surface air core vortices will occur:
S = Minimum submergence to prevent vortexing, in inches
D = Pump suction inlet diameter in inches
Q = Pump design flow rate, in USGPM
S = D + [( 0.574 x Q) /( D^1.5)]
Source: American National Standard for Pump Intake Design, Hydraulic Institute, ANSI/HI 9.8-1998,
Section 9.8.7
Q = 3200 GPM
D = 16”
S (Minimum submergence) = 44.7”
Q = 1000 GPM
D = 16”
S (Minimum submergence) = 25”