Volume of water in a chilled water system

Status
Not open for further replies.

imok2

Mechanical
Oct 21, 2003
1,311
Is there any way you can determine the volume of water in a closed chilled water system by the tonnage, discounting the volume by pipe size?
 
Replies continue below

Recommended for you

Quite simply, the answer is NO.

However, depending upon the type of duty, a minimum chilled water volume would probably be from 3 to 7 litres per kW cooling (which is about 10 to 20 litres per TonR).

If you want to determine the volume of an actual system, you need to dissolve a known quantity of something in it and then, after sufficient time has elapsed to ensure mixing, measure the concentration.

Regards,

Brian
 
briand2 Thanks for the response. I don't normally deal in liters but in gallons however I do know how to convert...I think...Just kidding
 