Some devices like some valve positioners and two wire loop powered transmitters, can only use a current signal because part of the current signal is used to drive the electronics of the device. If you use those devices, current is inescapable in the loop, although the inputs are expected to have a precision dropping resistor which then becomes a voltage to measure and troubleshoot from.
I prefer the live zero that 4-20mA or 1-5V provides versus the zero based low end. An open circuit is really obvious with the expectation of a live zero.
A voltage output has the benefit of paralleling to more than one input, which seems to be more intuitive to the uninitiated than a series loop for current outputs.