Follow up:
Well.
Scotty nailed it.
I went back to figure out how to isolate the stator windings taking a 6 digit Kelvin ohmmeter with me. I took the top off the 'generator box' to look at all the busbars where the stator cables land. There are two cross bars at different levels with 4 inch busbars. While pondering why I was seeing two stator cables landed on each bar, like a face slap with a mackerel, I realized there were FOUR busbars, each with two landed cables. Further inspection made me realize that the three 14AWG wires across the room in the control panel that I was reporting the badly different voltages across were not all going to the three Phase busbars. One was going to the 'fourth' busbar. In my defense the insides of the generator box is completely homogeneously coated in a hard gray/brown dust that does not blow-off but must be scraped off with a sharp tool. You can't see the ORANGE, YELLOW, RED tape indicating the phases on the big cables. Ney you cannot even see that there is marking tape.
Once the discrepancy was noted I scraped the ends of the three and only three 14AWG wires learning that they were W, U, and.... N.
Hence the 390/224/226 readings.
With that knowledge it became clearer that a transformer was not needed to get the 480 down to 277V the Vreg could swallow as I had 277V available.
I redid the 12V/field battery test getting 390.2/390.1/390.2V.
I proceeded to hook-up the already purchased and installed by others VR902 regulator. After spending a bunch of time finding a shunt trip breaker and installing it. I discovered whoever had initially mounted the regulator had just tossed a bag in the bottom of the enclosure that contained the bizarre shunt-trip (18VDC!) and a required voltage adjust 3,500Ω pot.
So I yanked my 100V~415V shunt-trip made a bracket to hold the factory shunt-trip and pot, soldered leads on the pot and wired it all up.
Checked the water level. A bit low. Checked the oil level about in the middle of the allowed range and surprisingly immaculate.
Walked back thru the power car to the F type locomotive past the 1,500HP prime mover and stuck my head out the door to tell the security guy to standby for some noise. Man. This is parked 100 feet from about hundred apartments and it's 8pm. Hopefully Monday Night Football will keep them distracted.
I back tracked and hooked up the brand new pair of batteries, battery leads to the Cummins starter. Turned on the fuel pump breaker. Set the engine switch to run. Noticed the main 700A breaker was off and left it that way. Pressed the starter switch and waited while the engine got it together. When it finally caught the sound was astounding. With headphones on it sounded like I was in a gunfight with only short barrel 44 magnums blazing away - point blank. I have never heard such a racket. Smoke started pouring out of the sides of the twin turbos. Which appeared to be covered with black oil.
After about 6 seconds of this sonic maelstrom the noise stopped replaced by a smooth but slow running engine. After about ten more seconds the engine smoothly accelerated to synchronous speed. The smoking turbos tapered off to no smoke and the black oil coating utterly vaporized to 'classic' rusted iron.
Measuring the voltage at the breaker was found to be 360V. Turning the voltage adjust pot up all the way resulted in 407V. The built-in
voltage range pot on the reg was adjusted until the voltage was 500V then the voltage was adjusted down to 480V with the voltage adj pot. Well actually since it was pretty course 479.6V. The balance was 479.6V/479.6V/479.6V. I don't think I've ever seen that balanced a set of readings.
I tried measuring the frequency but my meter completely spazzed-out showing 810Hz. I switched to a new clamp-on Klein meter. I clamped it around one of the big phase cables going to the breaker just to hold it. I turned the meter to Hz and it read 60.1Hz without even hooking the leads up?? When I hooked the leads across phases it too read garbage 1100Hz, 800Hz, etc. Once I got garbage it stayed garbage. I'd have to turn the meter back off then on then set it to Hz and it would show 60.1Hz again until I hooked the leads up. I don't get it.
By this time the engine was up to 120F. Still standing in a cloud of oil smoke I started wondering why the six foot diameter 20HP radiator fan was not running. I guessed maybe the main breaker had to be on. I decided to close the panel before trying that particular festivity. On closing it low and behold there was a large panel frequency meter reading 60Hz.
Both-handing the breaker lever closed there was a sudden hurricane blowing past me. The fan! Checked it and it felt smooth.
Temp got up to a steady 160F.
The room is surrounded by 200W light bulbs that didn't light up. Why? Had to dig out the breaker panel. No power found in it. There is a contactor that is twice the size of the main breaker in the generator control panel. It hooks the generator to the Head End Power bus when the ON-LINE knob is turned. Unfortunately a few days ago the yahoos incorrectly connected the HEP cable up and it came loose to be dragged by the train down the ties. That pulled half the wires loose and the pins out of the connector. Since that hadn't been repaired there was no way I was going to close on HEP. We'd done the whole job on drop lights from my truck via an inverter and a Milwaukee battery work light.
I shut it down and asked the security guard if he'd seen anyone with torches and pitch forks. He said AFTER the start it wasn't very loud really. "He'd actually forgotten about it after a few minutes." Guess the two 8 foot long 2 foot diameter mufflers do the trick.
The only thing left to do is load test it. I have no idea what the field current needs to be so my fuses may be wrong. I have no manual for the tail-end and not even a plate for the generator. My plan is to run the full train, about 10 cars, with heat and lights while measuring the field current. Add a fudge, factor and put those fuses in.
Thanks everyone for your support and guidance. It all went together to flesh-out a successful result.
Keith Cress