Hi,

In the thread 238-214018 Morquea mention a method and rule of thumb to dimention a transformer for motor starting. Basically consist on the following:

Calculate Motor Starting kVA = (FLA of motor)*sqrt(3)*(3 phase voltage)

Calculate SC level at the secondary of the transformer using transformer impedance.

Voltage drop = motor starting KVA / SC level kVA.

Now my questions:

Anyone can demostrate this rule?
This rule of thumb assume that the transformer is connected to an infinite SC capacity utility system. If i have the utility system SC capacity at the primary side of the transformer, how can i use it in the above rule of thumb to make a more precise calculation.

In my specific case i have a 1000 HP motor, connected to a 33/4.16 kV transformer. SC capacity at the primary side is 25 kA. There are no more MV motors connected to the secondary side.

Regards,
 
Replies continue below

Recommended for you

First of all some remarks:
1)In the formula Motor Starting kVA = (FLA of motor)*sqrt(3)*(3 phase voltage)
instead of FLA has to be LRA [Locked Rotor Ampere]
2) you have to recalculate the SC level using total impedance[System+Transf]and may the 4.16 cable up to motor terminals
Now revising the demonstration
OA=Vs
OB=VL*cosFi+R*I
AB=VL*sinFi+X*I
OA^2=OB^2+AB^2
Vs^2=(VL*cosFi+R*I)^2+(VL*sinFi+X*I)^2
Vs^2=(VL^2*cosFi^2+R^2*I^2+2*VL*cosFi*R*I)+(VL^2*sinFi^2+X^2*I^2+2*VL*sinFi*X*I)
VL=y
y^2*(cosFi^2+sinFi^2)+2*(cosFi*R*I+sinFi*X*I)*y+R^2*I^2+X^2*I^2-Vs^2=0
cosFi^2+sinFi^2=1
b=(cosFi*R*I+sinFi*X*I)
c=R^2*I^2+X^2*I^2-Vs^2
y^2+2*b*y+c=0
y=-b+/-sqrt(b^2-c)
Since y>0 then y=sqrt(b^2-c)-b
VL=sqrt((cosFi*R*I+sinFi*X*I)^2-R^2*I^2-X^2*I^2+Vs^2)-(cosFi*R*I+sinFi*X*I)
approximating:
(cosFi*R*I+sinFi*X*I)^2-R^2*I^2-X^2*I^2=0
VL=Vs-(cosFi*R*I+sinFi*X*I)
Vs-VL=(cosFi*R*I+sinFi*X*I)
Simplifying we'll put R=0 then
Vs-VL=sinFi*X*I per phase to neutral
or
As cos(fi) at start is approx. 0.3 sin(fi)=sqrt(1-0.09)=0.954
DeltaV=sqrt(3)*X*Istart*.95
X=Xsys+Xtrf X=VLL^2/Ssc
where Ssc = Apparent short-circuit power at motor terminal [from the system]
Istart=Sstart/sqrt(3)/VLL
where Sstart = Apparent power at motor terminal [from motor starting]
DeltaV=0.95*sqrt(3)*VLL^2/Ssc*Sstart/sqrt(3)/VLL
DeltaV=0.95*VLL*Sstart/Ssc
DeltaV/VLL%=95*Sstart/Ssc
1918x1.jpg
 
Thanks, now i feel confident in using the rule of thumb.
 