Suggestion to the previous posting marked ///\\\:
If you take two cables in parallel as opposed to one single conductor, the surface area is effectively higher on the two cables
///Agree\\ and so they can have a lower cross sectional area increasing the resistance
///Agree\\ and therfore increasing the voltage dop.
///This remains to be seen, since the heat dissipation Hd is dependent on conductor resistance, surface and current flowing through the conductor. Therefore, approximately:
Hd1 ~ R x I**2
now considering two subconductors and the current divided evenly to 1/2
Hd2 ~ 2 x R x (I/2)**2 = (1/2) x R x I**2
Therefore:
Hd2 ~ (1/2)Hd1
There will be smaller heat dissipation and smaller voltage drop.\\\