For 11 miles of 15 kV cable, you may want to also consider the capacitive reactance of the cable and resulting charging current. This is generally neglected in low voltage calculations, but could be of interest in 11 miles of cable. For 150A of load (what pf?), the charging current may not be too critical, but becomes more important as the cable gets longer and longer.
You would need a cable model that includes appropriate shunt capacitance in addition to the series inductance and resistance.