I agree with FreddyNurk regarding the ETAP analysis setup (use one as swing and the others in voltage-control mode). There are four parameters of concern in load flow analysis: voltage magnitude, voltage angle, active power, and reactive power. For each mode, two of these are held constant and two are allowed to vary as the nonlinear solver works the problem. This is because the two state variables are voltage magnitude and voltage angle at each bus, and the two input variables are active and reactive power. The swing (slack) generator keeps voltage magnitude and voltage angle constant at the bus, while allowing its active and reactive power to vary. Voltage-control mode (PV mode) is used to keep voltage magnitude constant on the bus and have constant active power flow out of those generators, while allowing bus voltage angle and reactive power output to vary. I think Mvar control mode is used for generators that would have constant active and reactive power flow and allow bus voltage magnitude and voltage angle to vary. This would be useful for modeling sources that can have specific active and reactive power flow commanded via setpoints.
I disagree with waross slightly for what to do in practice depending on the type of generator controllers available. Many modern generator controllers can be networked and will load share and regulate frequency and voltage via network communications, so you wouldn't need to run one isochronous and the rest in droop, or all in droop, and you wouldn't need cross-current compensation for var sharing if that's the case. The method waross stated is used in older control systems where individual generator controllers can't communicate with each other.
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips.