When calculating large anti-freeze solution systems (>40 gallons), does one need to consider the extreme daily minimum temperature, or the average daily minimum temperature?
On one particular project, AF sol'n at average daily minimum (20°F) is 30 psi under curve. At extreme daily minimum (-21°F), system is 100 psi over curve. A dry system is ~35 psi over the curve with pipe sizing to keep volumes under 750 gal capacity.
Which condition does one go with? The contract drawings state "layout and calculate per NFPA 13." RFI did not produce an answer. The AHJ is unsure. He thinks the extreme daily minimum may be excessive, but is doing his own research on the topic.
What does the collective here think?
Travis Mack